Forum

Share:
Notifications
Clear all

A2013 DEVICE OVERTEMP alarm in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
451 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2013 DEVICE OVER TEMP alarm in ABB ACSM1 Drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Measured drive temperature has exceeded internal alarm limit.

Check ambient conditions.
Check air flow and fan operation.
Check heatsink fins for dust pick-up.
Check motor power against unit power.

Reply
Share: