How can resolve problem A2017 FIELDBUS COMM alarm in ABB ACSM1 Drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Cyclical communication between drive and fieldbus adapter module or between PLC and fieldbus adapter module is lost.

Programmable fault: 50.02 COMM LOSS FUNCTION

Check status of fieldbus communication.

Check fieldbus parameter settings.

See parameter group 50 on page 207.

Check cable connections.

Check if communication master can communicate.