How can resolve problem A2022 ENCODER 1 FAILURE alarm in ABB ACSM1 Drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Encoder 1 has been activated by parameter but the encoder interface (FEN-xx) cannot be found.

Check parameter 90.01 ENCODER 1 SEL setting corresponds to encoder interface 1 (FEN-xx) installed in drive Slot 1/2 (signal 9.20 OPTION SLOT 1 / 9.21 OPTION SLOT 2).

Note: The new setting will only take effect after parameter 90.10 ENC PAR REFRESH is used or after the JCU control unit is powered up the next time.