Forum

Share:
Notifications
Clear all

A2030 RESOLVER AUTOTUNE ERR alarm in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
472 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2030 RESOLVER AUTO TUNE ERR alarm in ABB ACSM1 Drive ?

Topic Tags
1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Resolver autotuning routines, which are automatically started when resolver input is activated for the first time, have failed.

Check cable between resolver and resolver interface module (FEN-21) and order of connector signal wires at both ends of cable. Check resolver parameter settings. For resolver parameters.

Note: Resolver autotuning routines should always be performed after resolver cable connection has been modified.

Autotuning routines can be activated by setting parameter 92.02 EXC SIGNAL AMPL or 92.03 EXC SIGNAL FREQ, and then setting parameter 90.10 ENC PAR REFRESH to (1) Configure.

Reply
Share: