Forum

Share:
Notifications
Clear all

F0006 EARTH FAULT Fault in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
831 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0006 EARTH FAULT Fault in ABB ACSM1 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Drive has detected load unbalance typically due to earth fault in motor or motor cable.

Programmable fault: 46.05 EARTH FAULT

Check that there are no power factor correction capacitors or surge absorbers in motor cable.
Check that there is no earth fault in motor or motor cables:
- measure insulation resistances of motor and
motor cable.

Reply
Share: