F0012 BR OVERHEAT Fault in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
663 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0012 BR OVERHEAT Fault in ABB ACSM1 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Braking resistor temperature has exceeded fault limit defined by parameter 48.06 BR TEMP FAULT LIMIT.

Stop drive. Let resistor cool down.
Check resistor overload protection function
settings, parameters 48.01...48.05.
Check fault limit setting, parameter 48.06.
Check that braking cycle meets allowed limits.