Forum

Share:
Notifications
Clear all

F0032 OVERSPEED Fault in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
534 Views
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F0032 OVER SPEED Fault in ABB ACSM1 Drive ?

1 Reply
Posts: 14965
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Motor is turning faster than highest allowed speed due to incorrectly set minimum/ maximum speed, insufficient braking torque or changes in load when using torque reference.

Check minimum/maximum speed settings,
parameters 20.01 MAXIMUM SPEED and
20.02 MINIMUM SPEED.
Check adequacy of motor braking torque.
Check applicability of torque control.
Check need for braking chopper and resistor(s).

Reply
Share: