Forum

Share:
Notifications
Clear all

F0045 FIELDBUS COMM Fault in ABB ACSM1 Drive

2 Posts
1 Users
0 Reactions
853 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0045 FIELDBUS COMM Fault in ABB ACSM1 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Cyclical communication between drive and fieldbus adapter module or between PLC and fieldbus adapter module is lost.

Programmable fault: 50.02 COMM LOSS FUNCTION

Check status of fieldbus communication.

See appropriate User’s Manual of fieldbus adapter module.

Check fieldbus parameter settings.

See parameter group 50 

Check cable connections.

Check if communication master can communicate.

 

Reply
Share: