A104 ConvOverTemp Converter overtemperature alarm In ABB DCS800

2 Posts
1 Users
0 Reactions
762 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A104 ConvOverTemp Converter over temperature alarm In ABB DCS800 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Wait until the converter is cooled down. Shutdown temperature see MaxBridgeTemp (4.17). The converter overtemperature alarm will already appear at approximately 5°C below the shutdown temperature.
Check:
- ConvFanAck (10.20)
- FanDly (21.14)
- converter door open
- converter fan supply voltage
- converter fan direction of rotation
- converter fan components
- converter cooling air inlet (e.g. filter)
- converter cooling air outlet
ambient temperature
-  inadmissible load cycle
- connector X12 on SDCS-CON-4