A107 Motor 1 calculated fault in ABB DCS800 drive indicates that the drive's internal calculations have determined that Motor 1 is experiencing an overload condition. This means the motor is drawing more current than its rated capacity, which can lead to overheating and potential damage.
Troubleshooting Steps:
- Verify that the motor is not overloaded by checking the load torque and speed.
- Inspect the mechanical components for any signs of damage or wear.
- Ensure that the motor is receiving the correct voltage and frequency.
- Review the motor parameter settings, including the rated current, overload protection level, and thermal protection settings.