ABB DCS880 Drive Programming
Optimize your ABB DCS880 drive performance by configuring parameters like motor data, control mode, ramp times, and more. This guide provides a comprehensive overview for efficient setup.
Here is step by step programming of ABB DCS880 drive:
Step 1 – control wiring
Connect all control wiring for start/stop and speed reference. Below image show control wiring of DCS880 drive.
abb dcs880 simple start stop image
Step 2 – Power wiring
Connect input power wiring and motor wiring to the drive. Below image show power wiring of DCS880 drive.
Step 3 – Parameters
Below list show all parameter used in DCS880 drive programming.
Parameter restore
  96.15 62: Clear
Motor Data
  99.10 ……V Nominal mains voltage
  99.11 ……A Armature Current
  9912 ……V Armature Voltage
  99.13 ……A Field Current
  99.14 ……rpm Base Speed/Motor Speed
Start/Stop
  20.02 DI1 Field Start/Stop
  20.06 DI1 Armature Start/Stop
  20.04 DI1…DI6 OFF2 Source 1(emergency off)
  20.05 1 = Off3 inactive Emergency stop source
  20.08 1 = Off2 inactive Off2 source 2 (emergency off)
  20.13  Not selected Fault reset source
  20.34 None; inactive Mains contactor acknowledge source
Speed Reference
  22.11 4 AI1 scaled
ACC/DCC Time
  23.12 ……s Acceleration time 1
  23.13 ……s Deceleration time 1
Speed Limit
  30.11 ……rpm minimum speed
  30.12 ……rpm maximum speed
Step 4 – Testing and Verification
  1. Start the Motor: Once programming is complete, you can initiate motor operation using the start/stop buttons on the control panel or through external control signals if configured.
  2. Monitor Performance: Observe the motor's operation and verify it functions as intended. If adjustments are needed, return to parameter setting mode and fine-tune the settings