How can resolve problem F507 M1OverLoad Motor 1 calculated overload Fault In ABB DCS800 ?
1 Reply
Dec 25, 2021 9:38 am
Wait until the motor is cooled down. The motor fan will continue to work until the motor is calculated down under the alarm level. It is not possible to reset the fault as long as the motor remains too hot.
Check:
M1FaultLimLoad (31.04)
M1AlarmLimLoad (31.03)