Forum

Share:
Notifications
Clear all

F515 M1FexOverCur Motor 1 field exciter overcurrent Fault In ABB DCS800

12 Posts
2 Users
0 Reactions
8,279 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

In 99 group which value you feed 6.2 or 2.2 

1. Check field current in  parameter 1.30,

2. Are you use field weeaking

If you are not using field weeaking then set field current value 6.2 in 99 group then fault rectify.

Reply
1 Reply
(@jaivignesh1898)
Joined: 2 years ago

Active Member
Posts: 6

@click2electro sir I changed field bridge then during spinning speed starts decreasing from maximum speed it shows arm over current 

I checked thyristor all are ok

Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

1. Check armature current in group 1

2. If armature current value higher then motor rated value then reduce load.

3. If all are ok then need to change control card.

3. One more thing increase de-acceleration time then check.

Reply
Page 2 / 2
Share: