2310 Armature overcurrent Fault In ABB DCS880
How can resolve problem 2310 Armature overcurrent Fault In ABB DCS880 ?
The armature current has exceeded either 07.36 Drive DC overcurrent level or 31.44 Armature overcurrent level.
Check:
That the start-up data in group 99 corresponds to the motor rating plate and that the drive is matching the motor.
The setting of 07.36 Drive DC overcurrent level and 31.44 Armature overcurrent level.
The settings of the current controller in group 27 Armature current control.
The settings of current and torque limits in group 30 Control limits.
The motor and motor cables.
All connections in the armature circuit.
The incoming voltage for synchronizing. If the synchronizing voltage is not taken from the mains directly, but via a synchronizing transformer or the 230 VAC/115 VAC network, check that there is no phase shift between the same phases. Use an oscilloscope to verify.
The mains/branch fuses.
The thyristors.
That there are no contactors opening and closing in the motor cables.
That there are no power factor correction capacitors or surge absorbers between line reactor and drive.