ABB DCS880 Drive
1
Posts
1
Users
0
Reactions
71
Views
Oct 01, 2024 5:29 am
2330 fault in ABB DCS880 drive indicates Residual current detected. This means the drive has detected an unbalance typically due to a residual current in the motor or the motor cables.
- Check the settings of 31.17 Residual current detection source, 31.18 Residual current detection type, 31.19 Residual current detection level and 31.20 Residual current detection delay.
- Check the residual current transformer, if necessary change transformer or connected drive hardware.
- Check the insulation resistances of motor and motor cables. Disconnect the mains, verify safe isolation from supply in armature and field circuits and make insulation tests for the complete installation.