How can resolve problem 2330 Residual current detected Fault In ABB DCS880 ?
Programmable, see 31.18 Residual current detection type.
The drive has detected an unbalance typically due to a residual current in the motor or the motor cables. Sum of IL1, IL2, IL3 ≠ zero. See also A2B3.
Check:
− The settings of 31.17 Residual current detection source, 31.18 Residual current detection type, 31.19 Residual current detection level and 31.20 Residual current detection delay.
− The residual current transformer, if necessary change transformer or connected drive hardware.
− The insulation resistances of motor and motor cables. Disconnect the mains, verify safe isolation from supply in armature and field circuits and make insulation tests for the complete installation.