3280 Mains low voltage Fault In ABB DCS880

2 Posts
1 Users
0 Reactions
937 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 3280 Mains low voltage Fault In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Mains low (under-) voltage (AC side). See also A111. The firing angle is forced to 150° and single firing pulses to suppress the DC current are given.
Check:

The setting of 31.51.Mains loss mode, 31.52 Mains loss down time, 31.53 Mains loss low level 1 and 31.54 Mains loss low level 2.

That the mains voltage scaling is correct. See 99.10 Nominal mains voltage.

The cutting of the voltage coding resistors on the SDCS- PIN-H51.

The condition of the mains (voltage, cabling, fuses, switchgear).

That all 3 phases are present directly at the drive.