5080 Drive fan acknowledge Fault In ABB DCS880

2 Posts
1 Users
0 Reactions
277 Views
Posts: 14968
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem 5080 Drive fan acknowledge Fault In ABB DCS880 ?

1 Reply
Posts: 14968
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Programmable, see 31.41 Main fan fault function.

Drive cooling fan feedback at the DI is missing. See also A581.
Check:

The settings of 20.38 Drive fan acknowledge source and 20.40 Drive/Motor fan delay time.

The drive fan operation and connection.

The drive fan contactor.

The drive fan circuit.

The drive fan klixon.

The drive fan components.

The drive fan supply voltage.

The drive fan direction of rotation.

The drive door open.

The drive cooling air inlet (e.g. filter).

The drive cooling air outlet.

H7 an H8 pressure switch (setting should be 2 mbar).

The used digital inputs and outputs (groups 10 and 11)