How can resolve problem 7081 Control panel/PC tool link communication Fault In ABB DCS880 ?
1 Reply
Dec 25, 2021 8:43 am
Control panel/PC tool has stopped communicating. See also
A7EE.
Check:
− The setting of 49.05 Communication loss action.
− The control panel/PC tool connection cable.
− The control panel connector.
− The mounting platform if being used.
− Disconnect and reconnect the control panel/PC tool.
− Check the auxiliary code.
The code specifies the I/O port used as follows:
0: Panel/PC tool.
1: Fieldbus interface A.
2: Fieldbus interface B.
3: Ethernet.
4: D2D/EFB port.