Forum

Share:
Notifications
Clear all

71B1 Motor fan acknowledge Fault In ABB DCS880

2 Posts
1 Users
0 Reactions
800 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 71B1 Motor fan acknowledge Fault In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Programmable, see 20.39 Motor fan acknowledge source.

Motor/External cooling fan feedback at the DI is missing. See also A781.
Check:

The setting of 20.39 Motor fan acknowledge source.

The fan operation and connection. Replace the motor/external fan if faulty.

The fan contactor.

The fan supply voltage.

Reply