7310 fault in ABB DCS880 drive indicates Overspeed condition. This means the motor is turning faster than highest allowed speed due to incorrectly set minimum/maximum speed, insufficient braking torque or changes in load when in torque control.
- Check the settings of 30.11 M1 minimum speed, 30.12 M1 maximum speed and 31.30 M1 overspeed trip margin.
- Check the settings of the speed controller in group 25 Speed control.
- Check the setting of 46.02 M1 speed scaling actual.
- Check the torque control settings.
- For correct speed feedback when using an encoder or a tacho. Thus, compare the value of 90.01 Motor speed for control vs. the measured motor speed (hand held tacho).