Forum

Share:
Notifications
Clear all

73B0 Emergency ramp stop Fault In ABB DCS880

2 Posts
1 Users
0 Likes
296 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem 73B0 Emergency ramp stop Fault In ABB DCS880 ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Emergency stop did not finish within the expected time.
Check:

− The settings of 31.31 Emergency ramp supervision and
31.32 Emergency ramp supervision delay.

− The settings of parameters 23.11 ... 23.19 for Off3 stop
mode 1 (21.03 Emergency stop mode = Ramp stop).

− The setting of 23.23 Emergency stop time for Off3 stop
mode 2 (21.03 Emergency stop mode = Emergency ramp
stop).

− The current and torque limits in group 30 Control limits.

Reply
Share: