A112 P2P and M/F communication warning In ABB DCS880

2 Posts
1 Users
0 Reactions
414 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A112 P2P and M/F communication warning In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Peer to peer and master-follower communication loss. See also F544.
Check:

DCSLink node ID settings. See 70.05 DCSLink node ID.

The setting of 31.13 Fault stop mode communication and 70.07 DCSLink comm loss function.

The setting of 70.17 Mailbox 1 node ID, 70.23 Mailbox 2 node ID, 70.29 Mailbox 3 node ID and 70.35 Mailbox 4 node ID.

The setting of 70.18 Mailbox 1 cycle time/timeout, 70.24 Mailbox 2 cycle time/timeout, 70.30 Mailbox 3 cycle time/timeout and 70.36 Mailbox 4 cycle time/timeout.

The DCSLink cable connections.

The DCSLink terminations.