How can resolve problem A114 Armature current deviation warning In ABB DCS880 ?

1 Reply
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

7.02 Used current reference differs from 27.05 Motor current for longer than 5 sec by more than 20 % of nominal motor current. If the current controller cannot match the given current reference, the warning signal is created. Normally the reason is a too small incoming voltage compared to the motor EMF.

For non-motoric applications, it is possible to block the warning using 06.11.b07 Auxiliary control word 2.
Check:

For blown DC fuses.

The ratio between mains voltage and armature voltage (either the mains voltage is too low or the motor’s armature voltage is too high).

If the setting of 30.44 Minimum firing angle is too high.