A117 Armature current ripple warning In ABB DCS880

2 Posts
1 Users
0 Reactions
895 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A117 Armature current ripple warning In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

One or several thyristors may carry no current. See also F517.
Check:

The values of 01.50 Current ripple and 01.51 Current ripple
filtered1.

The setting of 31.46 Current ripple function and 31.47 Current
ripple level.

For too high gain of current controller. See 27.29 M1 current
proportional gain.

The positive/negative current feedback with an oscilloscope (6
pulses within one cycle visible?).

The thyristor gate-cathode resistance.

The thyristor gate connection.

The current transformers (T51, T52).

The condition of the mains (voltage, cabling, fuses,
switchgear).