A130 Mains phase loss warning In ABB DCS880

2 Posts
1 Users
0 Reactions
696 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A130 Mains phase loss warning In ABB DCS880 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Programmable Fault  31.21 Mains phase loss

One or several mains voltage phase(s) are missing. See also 3130. The firing angle is forced to 150° and single firing pulses to suppress the DC current are given.

Check:

The condition of the mains (voltage, cabling, fuses, switch-gear).

That all 3 phases are present directly at the drive.

H1 ... H5: measure the fuses F100 ... F102 on the SDCS-PIN-H01.

H6 ... H8: check and measure the connections XU1/XU2, XV1/XV2 and XW1/XW2 on the SDCS-PIN- H51.

For mains supply imbalance.

For loose mains cable connections.

That the mains contactor closes and opens.