How can resolve problem A130 Mains phase loss warning In ABB DCS880 ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Programmable Fault  31.21 Mains phase loss
One or several mains voltage phase(s) are missing. See also 3130. The firing angle is forced to 150° and single firing pulses to suppress the DC current are given.
Check:
The condition of the mains (voltage, cabling, fuses, switch-gear).
That all 3 phases are present directly at the drive.
H1 ... H5: measure the fuses F100 ... F102 on the SDCS-PIN-H01.
H6 ... H8: check and measure the connections XU1/XU2, XV1/XV2 and XW1/XW2 on the SDCS-PIN- H51.
For mains supply imbalance.
For loose mains cable connections.
That the mains contactor closes and opens.