How can resolve problem A6D1 FBA A parameter conflict warning In ABB DCS880 ?
1 Reply
Dec 25, 2021 7:09 am
Fieldbus adapter A (FBA A): The drive does not have a
functionality requested by a PLC or a requested functionality has
not been activated. See also 65A1.
The settings of parameter groups 50 Fieldbus adapter (FBA) and
51 FBA A settings are not set according to the fieldbus adapter or
the device has not been selected.
Check:
− The PLC programming.
− The settings of parameter groups 50 Fieldbus adapter (FBA)
and 51 FBA A settings.
− The configuration of the fieldbus adapter.