A6D2 warning in ABB DCS880 drive

1 Posts
1 Users
0 Reactions
22 Views
Posts: 18126
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

A6D2 warning in ABB DCS880 drive indicates FBA B parameter conflict. This means the drive does not have a functionality requested by a PLC or a requested functionality has not been activated.

  1. Check the PLC programming.
  2. Check the settings of parameter groups 50 Fieldbus adapter (FBA) and 54 FBA B settings.
  3. Check the configuration of the fieldbus adapter.