How can resolve problem F503 Armature overvoltage Fault In ABB DCS880 ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Too high voltage on the armature/DC side.

Check:

− If the setting of 31.50 Overvoltage level is suitable for the
system.

− The settings of the field current controller, EMF controller,
flux linearization in group 28 EMF and field current control.
E.g. field weakening is not activated.

− For too high field current (e.g. problems with field
weakening).

− If the motor was accelerated by the load.

− For overspeed.

− For proper speed scaling. See 46.02 M1 speed scaling
actual.

− For proper armature voltage feedback.

− The cutting of the voltage coding resistors on the SDCS-
PIN-H51.