F515 M1 field exciter overcurrent Fault In ABB DCS880

2 Posts
1 Users
0 Likes
1,173 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem F515 M1 field exciter over current Fault In ABB DCS880 ?

1 Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Motor 1 field exciter overcurrent.
Check:

− In case this fault happens during field exciter autotuning,
deactivate the supervision by setting 31.59 M1 field
overcurrent level = 325 %.

− The setting of 31.59 M1 field overcurrent level.

− The settings of the field current controller in group 28 EMF
and field current control.

− The connections of the field exciter.

− The insulation of cables and field winding.

− The resistance of the field winding.

− For fault messages at the field exciter itself (flashing LEDs),
04.26 M1 field exciter fault word and 04.36 M1 field exciter
warning word.