Cause : DSI Comm Loss comes when communications between the drive and the Modbus or DSI master device have been interrupted.
- Cycle power.
- Check communications cabling.
- Check Modbus or DSI setting.
- Check Modbus or DSI status.
- Modify using C125 [Comm Loss Action].
- Connecting I/O terminals C1 and C2 to ground may improve noise immunity.
- Replace wiring, Modbus master device, or control module.