Allen Bradley PowerFlex 527 Drive
1
Posts
1
Users
0
Reactions
260
Views
Mar 08, 2024 9:49 am
Cause : Decel Override comes when the drive is not following a commanded deceleration because it is attempting to limit bus voltage.
• Reprogram Bus Regulator Action to eliminate any “Adjustable Freq” selection.
• Reprogram Bus Regulator Action to Shunt Regulator and add external shunt.
• Correct AC input line instability or add an isolation transformer.
• Reset drive.