Fault 111 in allen bradley PowerFlex 70 drive

1 Posts
1 Users
0 Reactions
396 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Enable Hardware comes when safe-Off board is not installed and pins 3 and 4 of the Safe-Off Connector are not jumpered. If Safe-Off board is installed, verify that the hardware enable jumper is removed. 

  • Install Safe-Off board or jumper pins 3 and 4.
  • Locate and remove the enable jumper on the main control board. Refer to DriveGuard Safe-Off Option (Series B) for PowerFlex 40P and PowerFlex 70 AC Drives,