Cause : Motor Oload Pend comes when motor overload is pending. Parameter 308 [Output Current] is squared, scaled and integrated over time. When this integrated value exceeds 0.5, this Exception Event occurs.
The integrator's output can be viewed in Parameter 330 [Fault TP Data] when parameter 329 [Fault TP Sel] is set to 13 “Mtr OL Outpt”. The overload integration rate is affected by parameters 336 [Service Factor], 337 [Mtr I2T Curr Min], 338 [Mtr I2T Spd Min] and 339 [Mtr I2T Calibrat].
- Reduce mechanical load