Cause : Motor Stalled comes when the motor has stalled. These three conditions have occurred at the same time for the amount of time specified in parameter 373 [Motor Stall Time]:
• Drive is not stopped (parameter 150 [Logic State Mach] not equal to zero)
• Drive is on limit (parameter 304 [Limit Status] not equal to zero)
• Drive is at zero speed (parameter 155 [Logic Status], bit 13 [At Zero Spd] is set).
1. Increase torque limit
2. Reduce mechanical load