Fault 42 in allen bradley PowerFlex 700S

1 Posts
1 Users
0 Reactions
204 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : DC Bus Undervolt comes when bus voltage has fallen below the level configured by parameter 409 [Line Undervolts].

1. Verify the AC Line.
2. In frames 1-4, verify the precharge resistor is present. (With power off, there should be a resistance between DC+ and BR+).

In frames 5 & 6, check the precharge board for errors. See the precharge board LED for fault sequence.