Forum

Share:
Notifications
Clear all

Fault 69 in allen bradley PowerFlex 700S

1 Posts
1 Users
0 Reactions
110 Views
Posts: 14968
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : HiHp Bus WtchDog comes when Bus Communication Watchdog Error - communication has halted in the communication bus, causing the watch dog timer to expire.

1. Check fiber-optic connections between the Power Interface Circuit Board and Voltage Feedback Circuit Board.
2. Check connections between the Main Control Board and the Power Interface Circuit Board.
3. Replace the Voltage Feedback Circuit Board.
4. Replace the Power Interface Circuit Board.
5. Replace the Main Control Board.

Share: