Allen Bradley PowerFlex 753, PowerFlex 755, PowerFlex 755T & PowerFlex 755TS Drive
1
Posts
1
Users
0
Reactions
159
Views
Mar 14, 2024 5:24 am
Cause : Torq Prove Cflct comes when P1100 [Trq Prove Cfg] is enabled, these parameters must be properly configured first is P35 [Motor Ctrl Mode] and another is P125 [Pri Vel Fdbk Sel] and P135 [Mtr Psn Fdbk Sel] must be set to a valid feedback device.
- The feedback device does not have to be the same device.
- However, Open Loop and Simulation Feedback are not considered valid feedback devices.
- If parameters 125 and 135 are set to a feedback module, verify that the module parameters are set properly.
- On the module, the feedback loss action CANNOT be set to 0 “Ignore.” Does not work in PM FV mode.
- Does not work with single ended or channel A only encoders.