Cause : FluxAmpsRef Range comes when the value for flux amps determined by the Autotune procedure exceeds the programmed [Motor NP FLA].

  1. The value for flux amps exceeds the value programmed in P26 [Motor NP Amps], as calculated by the Autotune procedure.
  2. Check motor nameplate data against parameters P25 [Motor NP Volts] through P30 [Motor NP Power].
  3. The value for flux amps exceeds the value programmed in P26 [Motor NP Amps], as measured by the Static or Rotate Autotune procedure.
  4. Reprogram [Motor NP FLA] with the correct motor nameplate value.
  5. Repeat Autotune.