Forum

Share:
Notifications
Clear all

Fault code 14 in allen bradley PowerFlex 755 drive

1 Posts
1 Users
0 Reactions
274 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Ground Warning comes when a current path to earth ground has been detected at one or more of the drive output terminals. 

  • Check the motor and external wiring to the drive output terminals for a grounded condition.
  • The ground current has exceeded the level set in P467 [Ground Warn Lvl].
  1. A current path to earth ground greater than 25 % of drive rating has occurred.
  2. Check the motor and external wiring to the drive output terminals for a grounded condition.
  3. Check the programming.
  4. Check for excess load, and other causes of excess current. Insulation Resistance (IR) test the wiring to motor.
Share: