Fault code 17 in allen bradley PowerFlex 755 drive

1 Posts
1 Users
0 Reactions
266 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Input Phase Loss comes when the DC bus ripple has exceeded a preset level or missing input supply phase. This fault also comes when drive rectifier faulty.

The DC bus ripple has exceeded a preset level. Make these checks and adjustments in this order.

  1. Check input impedance balance.
  2. Increase the setting of P463 [InPhase Loss Lvl] to make the drive less sensitive.
  3. Tune the bus regulator or speed regulator to mitigate the effects of dynamic cyclic loads on DC bus ripple.
  4. Disable the fault by setting P462 [InPhase LossActn] to 0 “Ignore” and use an external phase loss detector such as a Bulletin 809S relay.
  5. Check incoming power for a missing phase/blown fuse.