Member
Cause : Phase UNegToGrnd comes when a phase to ground fault has been detected between the drive and motor in this phase. Rotate U/T1, V/T2, W/T3 connections.
  1. If the problem follows the wire, suspect a field wiring problem.
  2. If no change, suspect a problem with the drive.