Allen Bradley PowerFlex 753, PowerFlex 755, PowerFlex 755T & PowerFlex 755TS Drive
1
Posts
1
Users
0
Reactions
194
Views
Mar 14, 2024 5:34 am
Cause : Phase WNegToGrnd comes when a phase to ground fault has been detected between the drive and motor in this phase. Rotate U/T1, V/T2, W/T3 connections.
- If the problem follows the wire, suspect a field wiring problem.
- If no change, suspect a problem with the drive.