KEB COMBIVERT F6 drive fault codes
KEB COMBIVERT F6 drive fault codes - Fault codes for KEB COMBIVERT F6 drive controller series. Includes error codes, meanings, and suggested corrective actions.
To provide structured information about fault and warning codes generated by COMBIVERT F6 drives, including error identification, cause analysis, and troubleshooting guidance.
Below list shows fault codes and their solutions of KEB COMBIVERT F6 drive fault code:
ru01
Error text
Description
st01
no exception
No error
0x0000
3
ERROR overcurrent PU
Overcurrent detection in the power unit has triggered (e.g. short circuit, defective power module)
0x5400
4
ERROR overcurrent analog
Exceeded overcurrent level on the control board
(e.g. Incorrect setting of the controller or the torque lim- iting characteristic)
0x2300
5
ERROR over potential
Overvoltage in DC link
(e.g. deceleration ramp too fast, braking resistor not connected, braking transistor defective)
0x3210
6
ERROR under potential
Undervoltage in DC link
0x3220
7
ERROR overload
Module overload ( I2 t ) => OL
(long-term mean current load is above 100%)
0x3230
8
reset E. overload
Reset of overload possible OL counter (ru29) < 50% of the warning level
0x3230
9
ERROR overload 2
Module overload 2
(fast overload protection – defined by standstill continu- ous current and short time current limit - has re- sponded)
0x1000
10
ERROR overheat powmod.
Overtemperature power components (heat sink)
0x4210
11
reset E overheat pmod.
Overtemperature power components decreased (tem- perature 5° below OH level)
0x4210
12
ERROR overheat internal PU
Overtemperature internal power unit
0x4110
13
reset E. overheat intern PU
Overtemperature internal power unit decreased
0x4110
14
ERROR motorprotection
electronic (software) motor protection has triggered
0x1000
15
reset E. motorprotection
Error motor protection function can be reset
0x1000
16
ERROR drive overheat
Temperature sensor in the motor (e.g. PTC or KTY) has triggered
0x4310
17
reset ERROR drive overheat
Overtemperature motor decreased
0x4310
ru01
Error text (continuation)
Description
st01
18
ERROR overspeed
Overspeed
(speed > pn26 * rated speed)
0x1000
20
ERROR drive data
Error at presetting motor data
(Standardization of the motor data triggers an error
=> motor data do not match)
0x1000
21
ERROR motordata not stored
Motor data are not confirmed by dr99
0x1000
22
ERROR ident
during identifikation an error occured (Information about the type of error in dr57)
0x1000
23
ERROR speed diff
Speed difference higher than level
(the monitoring of the difference between the set- point speed and actual speed within a configurable time has responded pn38..pn41)
0x1000
24
ERROR fieldbus memory
Incorrect drive software configuration
0x1000
38
ERROR memory size
0x1000
40
ERROR FPGA conf.
Error in FPGA configuration
0x1000
41
ERROR safety module SACB comm
No communication with the safety module (only control type A or P)
0x1000
42
ERROR power unit SACB comm
No communication with the power unit (from hous- ing size 6)
0x1000
43
ERROR enc.intf. SACB comm.
No communication with encoder interface
0x1000
44
ERROR invalid power unit data
Invalid power unit data
0x1000
47
ERROR power unit flash
The plausibility check of the Flash memory of the power unit CPU has reported an error
0x1000
52
ERROR undervoltage phase
Phase failure at the mains input (L1,L2,L3)
0x1000
55
ERROR safety
The safety module has reported an error (only for control type A or P)
0x1000
56
ERROR software switch left
Software limit switch has triggered an error
0x1000
57
ERROR software switch right
0x1000
58
ERROR fieldbus watchdog
Fieldbus watchdog has responded
0x1000
59
ERROR prg. input
External error was triggered via programmable digi- tal input
0x1000
60
ERROR safety module type changed
The safety module has been replaced without au- thorisation
0x1000
61
ERROR safety module changed
0x1000
62
ERROR power unit changed
Power unit changed (de20 / de21)
0x1000
63
ERROR enc. intf. changed
Changed encoder interface (de48)
0x1000
64
ERROR power unit type changed
Power unit type changed (de26 / de27)
0x1000
65
ERROR enc. intf. version
Invalid version of the encoder interface
0x1000
66
Overcurrent
0x1000
67
ERROR max acc/dec
Max. acceleration/deceleration setting exceeded (monitoring especially necessary for cyclic synchro- nous operating modes)
0x1000
ru01
Description
st01
68
ERROR overcurrent Brake
Overcurrent at the brake output
0x1000
83
ERROR Limit Switch Forward
positive (hardware) limit switch released
0x1000
84
ERROR Limit Switch Reverse
negative (hardware) limit switch released
0x1000
85
ERROR Override Limit Switch For- ward
positive (hardware) limit switch override out of the range of hm19
0x1000
86
ERROR Override Limit Switch Re- verse
negative (hardware) limit switch override out of the range of hm20
0x1000
87
ERROR Limit Switch
Ether both (hardware) limit switches released or one (hardware) limit switch released and only the actual direction of rotation corresponds to the limit switch direction
0x1000
89
ERROR at encoder type change
Incompatible encoder interface and drive software versions
0x1000
90
ERROR enc.intf.fast comm.
Communication error control board-encoder inter- face
0x1000
91
init encoder interface
Encoder interface in initialisation routine
0x1000
92
ERROR encoder A
Error encoder A
Hardware defect or incorrect setting of the encoder parame-
ters (type, increments per revo- lution, etc.)
0x1000
93
ERROR encoder B
Error encoder B
0x1000
94
init encoder A
Initialisation encoder A is running
0x1000
95
init encoder B
Initialisation encoder B is running
0x1000
96
ERROR encoder missing
No encoder type is selected in ec16 in a mode that requires an encoder
0x1000
97
ERROR overspeed (EMF)
pn72 overspeed level (EMF) has been exceeded
0x1000
98
ERROR encoder A changed
Encoder A changed
Serial number read by the encoder is not equal to the stored serial number (ec48 != ec49)
0x1000
99
ERROR encoder B changed
Encoder B changed
0x1000
100
ERROR overcurrent out1
Overcurrent at digital output 1
0x1000
101
ERROR overcurrent out2
Overcurrent at digital output 2
0x1000
102
ERROR overcurrent out3
Overcurrent at digital output 3
0x1000
103
ERROR overcurrent out4
Overcurrent at digital output 4
0x1000
105
ERROR overcurrent encoder
Overcurrent at encoder interface
0x1000
106
ERROR overcurrent 24V
Overcurrent at 24V outputs of the control terminal block
0x1000
107
ERROR over frequency
The maximum output frequency de120 has been exceeded. (599Hz)
0x1000
108
reset E. overheat intern CB
Overtemperature control board decreased
0x1000
109
ERROR overheat internal CB
Overtemperature internal control board
0x1000
110
ERROR OH ramp
Maximum available time between the occurrence of an overtemperature error and the modulation switching off has expired
0x1000
111
ERROR OHI ramp
0x1000
112
ERROR 24V supply low
24V supply has dropped to a value lower than 18V
0x1000
ru01
Description
st01
115
ERROR GTR7 always OFF
Braking transistor can no longer be switched on
0x1000
116
ERROR GTR7 OC
UCE monitoring braking transistor reports OC
0x1000
117
ERROR GTR7 always ON
Braking transistor can not be switched off
0x1000
118
OC at 5V diag
Short circuit of 5V at the diagnostic interface
0x1000
119
ERROR extreme overpotential
extreme overpotential in DC link
(can lead to damage of the DC capacities)
0x3210
120
ERROR DC capacitor damaged
DC capacities have been damaged by too long / too high overvoltage in the DC link
0x1000
121
ERROR runtime
Activation of too many functions. => Runtime moni- toring
0x1000
122
ERROR UP2
Error, if the change of the state machine to "switched on" is requested and after the delay time in ru04 supply unit state the state "run“ is not yet reached.
0x1000
123
ERROR LT ready
an error is triggered if the "ready" signal of the power unit disappears during activated modulation.
0x1000
124
General Fielbus Error
(Analysis via parameter fb91 fieldbus error code)
0x1000
125
ERROR fieldbus type changed
The selected fieldbus type in fb68 fieldbus selection has been changed and no PowerOn reset has been performed yet
0x1000
126
ERROR overheat 2 powmod.
Overtemperature heat sink (2)
0x4210
127
reset E. overheat 2 pmod.
Overtemperature heat sink (2) decayed
0x4210
128
ERROR overheat 3 powmod.
Overtemperature heat sink (3)
0x4210
129
reset E. overheat 3 pmod.
Overtemperature heat sink (3) decayed
0x4210
130
ERROR overheat 2 internal
Overtemperature internal (2)
0x4210
131
reset E. overheat 2 intern
Overtemperature internal (2) decayed
0x4110
132
ERROR overheat 3 internal
Overtemperature internal (3)
0x4110
133
reset E. overheat 3 intern
Overtemperature internal (3) decayed
0x4110
134
ERROR Safety Stop
Safety module signals reaction SS1 or SS2
0x1000
135
ERROR File Code
Only P card: invalid file code
0x1000
136
ERROR blockade detected
ERROR drive blockade triggered
0x1000
139
ERROR STO
STO triggered by the safety module
0x1000
140
ERROR Fail Safe
Fail Safe triggered by the safety module
0x1000
141
ERROR control hardware type
inadmissible combination of control cards hardware and software
0x1000
142
ERROR speed search and rotor de- tection
inadmissible combination of the "speed search" and "system position measurement" functions, only in encoder mode
0x1000
144
ERROR overheat braking resistor
The temperature of the sub-mounted braking resis- tor has exceeded the error level
0x1000
ru01
Description
st01
145
ERROR invalid resistor data
invalid data for the sub-mounted braking resistor
0x1000
146
ERROR analog input 4..20mA
Monitoring of the 4..20mA interface has triggered an error (with appropriate programming)
0x1000
Configurable errors
The behaviour can be programmed for the following errors:
Index
Id-Text
Name
Possible error response
Fault
Fault ramp
Stop ramp
Warning / Ignore
0x2A04
pn04
ERROR OL stop mode
x*
x
0x2A08
pn08
ERROR OH stop mode
x*
x
0x2A0A
pn10
ERROR OHI stop mode
x*
x
0x2A0C
pn12
ERROR dOH stop mode
x*
x
x
x
0x2A10
pn16
ERROR OH2 stop mode
x*
x
x
x
0x2A14
pn20
ERROR SW-switch stop mode
x
x
x
x*
0x2A16
pn22
ERROR fb watchdog stop mode
x
x
x
x*
0x2A1B
pn27
ERROR overspeed stop mode
x*
x
x
x
0x2A1D
pn29
prg. error stop. mode
x
x
x
x*
0x2A22
pn34
ERROR encoder A stop mode
x*
x
0x2A23
pn35
ERROR encoder B stop mode
x
x*
0x2A25
pn37
ERROR max acc/dec stop mode
x
x
x
x*
0x2A28
pn40
ERROR speed diff stop mode
x
x
x
x*
0x2A47
pn71
E. overspeed (EMF) st. mode
x*
x
x
x
0x2A49
pn73
E.enc A changed stop mode
x
x
x*
0x2A4A
pn74
E.enc B changed stop mode
x
x
x*
0x2A4D
pn77
E.UP2 stopping mode
x
x*
0x2A4E
pn78
ERROR limit switch forward reaction
x
x
x
x*
0x2A4F
pn79
ERROR limit switch reverse reaction
x
x
x
x*
0x2A50
pn80
safety stop mode
x
x
x
x*
0x2A51
pn81
warning OH stop mode
x
x
x
x*
0x2A52
pn82
warning OHI stop mode
x
x
x
x*
0x2A56
pn86
E.AnIn stop mode
x
x
x
x*
0x2A59
pn89
warning brOH stop mode
x
x
x
x*