AL14 Earth Fault in Danfoss drive indicates that the drive has detected a ground fault in the motor or its wiring. This means there is an unintended connection between one or more of the motor phases and the ground, which can cause dangerous currents to flow, potentially damaging the drive, motor, or other components in the system.

"A14" alarm  in Danfoss devices indicate an "earth fault" or short circuit to ground. This means the insulation on the motor windings or cables may have deteriorated or been damaged, causing a short circuit to the ground.

Potential Causes of A14 Earth Fault:

  • Damaged Wiring: Faulty or damaged wiring can create a short circuit to ground.
  • Contamination: Foreign objects or contaminants can cause a short circuit.
  • Internal Component Failure: A faulty component within the device can lead to an earth fault.
  • Environmental Factors: Extreme temperatures, humidity, or corrosive environments can contribute to electrical faults.

Troubleshooting Steps:

  1. Visual Inspection:
    • Check for any visible signs of damage, corrosion, or loose connections in the wiring and components.
    • Look for any signs of liquid or contaminant intrusion.
  2. Check for External Factors:
    • Ensure that the device is operating in a suitable environment and is protected from excessive heat, humidity, or corrosive substances.
  3. Measure Insulation Resistance:
    • Use an insulation tester to measure the insulation resistance between the device's terminals and ground. A low resistance reading indicates a short circuit.
  4. Replace Faulty Components: If the insulation resistance test reveals a short circuit, identify and replace the faulty component.