EEPROM FAULT - Software cannot store any data changes.

OFF 2 (Serial data interface only) - Motor coast followed by relay off.

OFF 3 (Serial data interface only) - Quick stop followed by relay off.

START INHIBIT (Serial data interface only) - Start is inhibited until control word bit 0 is toggled.

UNIT READY (LOCAL) - Control card power section is powered up and okay.

ENABLED STOP (LOCAL) - Unit ready and motor coast inverse signal is on. No warning, is present; no start signal applied.

START (LOCAL) - Enable and start signal applied; no or too low reference signal or motor current.

HOLD - Start signal is applied, but ramping is blocked (serial data interface only).

RUN OK (LOCAL) - Unit is running on reference and in range.

JOGGING (LOCAL)

RAMPING (LOCAL)

FREEZE Reference is "frozen"; change possible by speed UP/DOWN.

RUN OUT RANGE Unit is running on reference, but out of the range set up by menus (either current or frequency), such as High Frequency, Low Frequency, Current, etc.

CURRENT LIMIT

NO MOTOR Enabled, but DC test shows that no motor is connected.

REF FAULT 4-20 mA signal not okay. NO 24 VOLT Internal power supply is not operational.

INVERT TIME (ETR) - Electronic inverter protection close to limit.

MOTOR TIME (ETR) - Electronic motor protection close to limit. At 97% the warning is given, at 100% a trip will occur.

VOLTAGE LOW - VOLTAGE HIGH The control card registers that the DC bus voltage is out of limits. Power section is running

STALLING - Short-term interruption of operation; ride through is attempted.

AUTOSTART - Operation is stopped; unit will attempt restart.

• TRIP (LOCKED) - Operation is stopped; external manual reset required. When the trip is locked, reset can only be accomplished by cycling AC power on and off.

Alarms Message

INVERTER FAULT - Power section NOT OKAY.

MAINS PHASE FAULT (loss of line phase)

OVER VOLTAGE-UNDER VOLTAGE - Power section has stopped the inverter due to voltage limits exceeded.

OVER CURRENT - Power section has stopped the inverter due to short circuit,

GROUND FAULT - Power section has stopped the inverter due to ground leakage.

OVER TEMP - Power section has stopped the inverter due to high heatsink temperature.

OVER LOAD (ETR) - Unit has been running too long at intermittent current.

MOTOR TRIP (ETR or THERMISTOR)

• Motor has been running too long at intermittent current.

KEY DISABLED - The inverter is in Factory set Mode, parameter 001.