Warning /Alarm 99 in Danfoss VLT FC301/ FC302 : Locked Rotor - comes when he rotor is blocked. Check if the motor shaft is locked.

1. Check if the start current triggers the current limit set in parameter 4-18 Current Limit.

2. Check if it increases the value in parameter 30-23 Locked Rotor Detection Time [s].