Forum

Share:
Notifications
Clear all

Warnings /Alarms 47 Control voltage fault in VLT Micro Drive FC51

3 Posts
2 Users
0 Reactions
1,621 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Warnings /Alarms 47 Control voltage fault in VLT Micro Drive FC51 - comes when 24 V DC is overloaded due to incorrect wiring of control card.

1. First power of drive and remove all control connection.

2. After remove control connection check fault coming or not.

2 Replies
Posts: 1
(@sunil-reddy)
New Member
Joined: 2 months ago

Yes Comming

Reply
1 Reply
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 18313

@sunil-reddy if same fault comes then hardware issue in drive. Need to repair or replace drive.

Reply
Share: