WARNING/ALARM 2 in danfoss iC2 micro drive
Cause : Live zero error- This warning or fault only appears if programmed in P 9.5.6.2 Live Zero Timeout Function. The signal on 1 of the analog inputs is less than 50% of the minimum value programmed for that input. Broken wiring or a faulty device sending the signal can cause this condition.
  • Check connections on all the analog input terminals. Control card terminals 33 and 34 for signals, terminal 35 common.
  • Check that the drive programming and switch settings match the analog signal type.
  • Perform an input terminal signal test.