WARNING/FAULT 10 in danfoss iC2 micro drive

1 Posts
1 Users
0 Reactions
188 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Motor overload temperature comes when the electronic thermal protection (ETR), the motor is too hot. Select whether the drive issues a warning or an alarm when the counter reaches 100% in P 4.6.7 Motor Thermal Protection. The fault occurs when the motor runs with more than 100% overload for too long.

  • Check if the motor is overheating.
  • Check if the motor is mechanically overloaded.
  • Check that the motor current set in P 4.2.2.3 Nominal Current is correct.
  • Ensure that the motor data in P 4.2.2.1 Nominal Power to P 4.2.2.5 Nominal Speed is set correctly.
  • Running AMA in P 4.2.1.3 AMA Mode tunes the drive to the motor more accurately and reduces thermal loading.